Default Anyone an electrician?

I figure there are quite a few do it your selfers on here, so I thought I would ask. I am asking everywhere I can think. So I had to replace a breaker in my breaker box today and I have a question. The breaker controlled the ceiling fan/light and all the outlets in a spare bedroom. Only thing in this room is a old computer I set up and is just used for storage on my network. Well it turned out that the ceiling fan/light in my daughters room and one of her outlets was also on this breaker. She had started running a space heater in her room which she happened to have plugged into that outlet. It apparently killed the breaker. It wasn't a standard 15 amp breaker it is one of those ground fault breakers with a test switch. From what I can find those need only be used for outside outlets or in bathrooms. I went to Lowes today and bought a 15 amp breaker and put it in and it's working fine. I am just wondering if I really need to get one of those ground fault type. The standard breaker was $3.75, a ground fault breaker is $41.00.

So why would they use one of those type breakers for a bedroom.
__________________
2013 Vision Sunset Red - Stage 1 exhaust, VictoryHID Cyclops
2004 Kingpin - Traded
Term is offline   Reply With Quote
Sponsored Links
Advertisement
 
Old 11-28-2012, 11:25 PM   #2
GatorJoe
Lifetime Premium
 
GatorJoe's Avatar
 
Join Date: Oct 2012
Location: Lake City, FL
Posts: 708
Garage
Default

Should be okay with a standard breaker simplest way of testing is put your hand on it when know is loaded up if doesn't feel overly warm you are fine .. Simply put, Circuit Breakers trip when heated .. My guess someone put one in the bedroom might have had a spare left over ..
__________________
2012 Victory Cross Country, Freedom Performance Duals, Lloyds Filter, ATS+4, VM1 Cams ,PCV Tuned by KMC ..
GatorJoe is offline   Reply With Quote
Old 11-29-2012, 04:39 AM   #3
gibson
Lifetime Premium
 
gibson's Avatar
 
Join Date: Jan 2012
Location: North east Indiana
Posts: 1,014
Default

Add up all the watts you are using on the circuit. That is why you are popping the breaker. http://www.wisegeek.com/how-much-ene...eaters-use.htm breakers protect the wire in the wall. Melted wire cause fires. The space heater should be on a different circuit. So add up the watts divide it by 120 = amps example: 1500+ 300+ 200=2000 / 120 = 16.666 amps Space heater+pc+ fan = 2000 any thing else turned on will overload the circuit...

Last edited by gibson; 11-29-2012 at 04:44 AM.
gibson is offline   Reply With Quote
Old 11-29-2012, 05:13 AM   #4
saddlebag
Lifetime Premium
 
saddlebag's Avatar
 
Join Date: Jun 2011
Location: Dayton, Ohio
Posts: 5,416
Default

Quote:
Originally Posted by Term View Post
I figure there are quite a few do it your selfers on here, so I thought I would ask. I am asking everywhere I can think. So I had to replace a breaker in my breaker box today and I have a question. The breaker controlled the ceiling fan/light and all the outlets in a spare bedroom. Only thing in this room is a old computer I set up and is just used for storage on my network. Well it turned out that the ceiling fan/light in my daughters room and one of her outlets was also on this breaker. She had started running a space heater in her room which she happened to have plugged into that outlet. It apparently killed the breaker. It wasn't a standard 15 amp breaker it is one of those ground fault breakers with a test switch. From what I can find those need only be used for outside outlets or in bathrooms. I went to Lowes today and bought a 15 amp breaker and put it in and it's working fine. I am just wondering if I really need to get one of those ground fault type. The standard breaker was $3.75, a ground fault breaker is $41.00.

So why would they use one of those type breakers for a bedroom.
You've got me puzzled.

1) A circuit breaker lives in a box somewhere with all its circuit breaker family

2) A GFI outlet lives on a wall in a room

3) Causing either one to trip can be remedied by resetting it. Why would you buy a new one?

4) GFI detects the difference in current flowing out of one terminal and back into the other terminal. If a human becomes part of a circuit and a portion of the current is going to them and into the ground rather than returning through the outlet's neutral, the GFI detects it. They are generally used near water. A circuit breaker only detects total current. It will not cut the juice if you become a Christmas light until you draw enough current to trip it. By then you'll be as dead as a Christmas goose.
__________________
http://www.victoryforums.com/signaturepics/sigpic6903_1.gif
2011 Cross Roads
saddlebag is offline   Reply With Quote
Old 11-29-2012, 07:56 AM   #5
BigRedXerII
Member
 
BigRedXerII's Avatar
 
Join Date: Oct 2010
Location: Southern Indiana
Posts: 84
Default

Quote:
Originally Posted by Term View Post
I figure there are quite a few do it your selfers on here, so I thought I would ask. I am asking everywhere I can think. So I had to replace a breaker in my breaker box today and I have a question. The breaker controlled the ceiling fan/light and all the outlets in a spare bedroom. Only thing in this room is a old computer I set up and is just used for storage on my network. Well it turned out that the ceiling fan/light in my daughters room and one of her outlets was also on this breaker. She had started running a space heater in her room which she happened to have plugged into that outlet. It apparently killed the breaker. It wasn't a standard 15 amp breaker it is one of those ground fault breakers with a test switch. From what I can find those need only be used for outside outlets or in bathrooms. I went to Lowes today and bought a 15 amp breaker and put it in and it's working fine. I am just wondering if I really need to get one of those ground fault type. The standard breaker was $3.75, a ground fault breaker is $41.00.

So why would they use one of those type breakers for a bedroom.
Not sure why they would have a ground fault in the bedroom. It's hard to second guess why somethings things get done a certain way.
I have been in constuction my whole life and still get amazed sometimes what people get by with or do.
If the 15amp works I would stick with that. You have to be carefull just moving up to the next breaker size, 20amp. If the wiring is not heavy enough at least 12 wire you can melt the wire and not trip the breaker.

Saddlebag you can buy a GFI breaker. It can be cheaper to use sometimes than GFI plugs. They get used alot on temporary poles on constuction sites.
__________________
'68 5hp Tote Goat minibike - My 1st Ride
'82 GS550L Suzuki - long gone
'91 1100 Shadow - gone
'91 900RR - gone
'02 1800 VTX Retro - Looking for a new home
'11 Cross Country - new ride looking new for twisties


"Its about the Journey and the Friends we make."
BigRedXerII is offline   Reply With Quote
Old 11-29-2012, 08:00 AM   #6
saddlebag
Lifetime Premium
 
saddlebag's Avatar
 
Join Date: Jun 2011
Location: Dayton, Ohio
Posts: 5,416
Default

Quote:
Originally Posted by BigRedXerII View Post
Saddlebag you can buy a GFI breaker. It can be cheaper to use sometimes than GFI plugs. They get used alot on temporary poles on constuction sites.
I see. Thanks.
__________________
http://www.victoryforums.com/signaturepics/sigpic6903_1.gif
2011 Cross Roads
saddlebag is offline   Reply With Quote
Old 11-29-2012, 08:33 AM   #7
ridealittle
Senior Member
 
Join Date: Aug 2012
Location: east tn near mountains
Posts: 462
Default

make sure there isn't a plug in the kitchen or bath or outside plug or fixture run off the ground fault, or a hot tup or spa. if you're ABSOLUTELY positive there are none you don't need a gf breaker. also a gf shouldn't trip as long as the total amps are ok. they shouldn't trip because a certain type of appliance is plugged in unless it has a -ground fault- losing power to ground instead of back to neutral.
__________________
now , 2011 crossroads
in order of ownership, sears compact scooter, honda 305 scrambler, honda 160 dream , triumph 500 trophy trail, honda cb450, sportster, honda f750, 2nd sportster, harley flh, harley super glide, 3rd sportster, bmw k1000, harley low rider, 2nd harley super glide, harley heratage, harley road king,
thats just the street bikes!
ridealittle is offline   Reply With Quote
Old 11-29-2012, 09:15 AM   #8
Term
Senior Member
 
Term's Avatar
 
Join Date: Sep 2012
Location: Georgia
Posts: 429
Default

Quote:
Originally Posted by ridealittle
make sure there isn't a plug in the kitchen or bath or outside plug or fixture run off the ground fault, or a hot tup or spa
I checked that, at first I thought maybe the back flood light was on the circuit but it wasn't. I checked every outlet in all the bathrooms.

Quote:
Originally Posted by saddlebag
1) A circuit breaker lives in a box somewhere with all its circuit breaker family

2) A GFI outlet lives on a wall in a room
I thought the same thing until this happen. I have not had one of these type breakers any any house I owned up to now. Only owned two before this, first built in the 70s and the second in the mid 80s.

Quote:
Originally Posted by gibson
Add up all the watts you are using on the circuit. That is why you are popping the breaker.

Thanks for all the replies. I understand why it tripped, it was my daughter using the space heater. Also that one outlet in her room had a TV and an X-BOX connected to it. That is taken care of. I just can't figure why they used a GFI breaker. Why I couldn't just reset it I don't now, a guy at Lowes told me the GFI breakers were a bit more sensitive and once they trip they can stop working. At $41.00 dollars a pop I think I will take my chances with a standard 15 amp breaker.
__________________
2013 Vision Sunset Red - Stage 1 exhaust, VictoryHID Cyclops
2004 Kingpin - Traded
Term is offline   Reply With Quote
Old 11-29-2012, 09:30 AM   #9
cornfedboy2000
Senior Member
 
cornfedboy2000's Avatar
 
Join Date: Feb 2012
Location: Oshkosh, WI
Posts: 352
Garage
Default

Just throwing this out there, gfi breakers and outlets alike can go bad causing them to blow unnecessarily.
cornfedboy2000 is offline   Reply With Quote
Old 11-29-2012, 10:46 AM   #10
wesdalton
Senior Member
 
wesdalton's Avatar
 
Join Date: May 2010
Location: Utah
Posts: 582
Default

The new building code (at least here in Utah) require ground fault breakers in bedrooms.
__________________
2010 X C
wesdalton is offline   Reply With Quote
Sponsored Links
Advertisement
 
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Powered by vBadvanced CMPS v3.2.2

All times are GMT -5. The time now is 11:41 PM.


Powered by vBulletin® Copyright ©2000 - 2014, Jelsoft Enterprises Ltd.
Garage Plus vBulletin Plugins by Drive Thru Online, Inc.
Motorcycle News, Videos and Reviews
Honda Grom Forum Harley Davidson Forum Honda 600RR Kawasaki Forum Yamaha R6 Forum Yamaha FZ-09 Forum
1199 Panigale Forum Roadglide Forum Honda CBR1000 Forum Vulcan Forum Yamaha R1 Forum Yamaha R3 Forum
Ducati Monster Forum Harley Forums Honda CBR250R Forum ZX10R Forum Star Raider Forum Yamaha Viking Forum
Suzuki GSXR Forum V-Rod Forums Honda Shadow Forum Kawasaki Motorcycle Forum Star Warrior Forum KTM Duke 390 Forum
SV650 Forum BMW S1000RR Forum Honda Fury Forum Kawasaki Versys Forum Drag Racing Forum Ducati 899 Panigale Forum
Suzuki V-Strom BMW K1600 Triumph Forum Victory Forums Sportbikes BMW NineT Forum
Volusia Forum BMW F800 Forum Triumph 675 Forum MV Agusta Forum HD Street Forum Suzuki GW250 Forum
Yamaha Motorcycles Victory Gunner Forum Honda Vultus Forum HD LiveWire Forum